support display 'OAR_Phase_Confirm_SD' Passwords and acknowledgement button is not responding from DeltaV Live

I am working on DeltaV Operate to Live migration project. 

In Phase prompt OAR action for confirm and Verify , passwords and acknowledgement button is not responding  from Live. if i am putting  the wrong password then not showing error message on screen but Username and Password works in correct manner when we acknowledge the same prompt from BOI.

So if anyone has faced the similar kind of issue, please share your experience or if someone knows how to deal with acknowledge button scripting changes in Live or is it issue into $Std_Esig_Confirm_Ctrl GEM or where which parameter needs to change. please share.

Please see below image of OAR display

3 Replies

  • Check these items:

    1. Ensure the Signatures Policies enable in System Preferences on the ProPlus
    2. Right Click on the ElectronicSignatures under Setup\Security and ensure the Enable Electronic Signatures for Live (if you have v14), Operate and Control Studio is checked.
    3. Right click on the area this unit exists in and make sure the Electronic Signature is enabled.
  • In reply to Matt Stoner:

    Many Thanks Matt
  • In reply to ktidke:

    I have enabled above option and download changed setup data but its still not working.
    I am trying to investigate it. I have found In acknowledge button " esigParamPath = strTag + '/PCSD_VERIFIER.CV'; " PCSD_VARIFIER parameter use in script. Should we need to add into unit module?