We have a requirement such that when Alarm List graphic is open & Acknowledge All button pressed from DeltaV Operate then it should Acknowledge All Alarms except Critical Alarms. Same applies to all graphics.
This requirement is because the Critical Alarms are most important & All Critical Alarms should not be Acknowledged at same, but one by one critical alarm will be acknowledged after taking proper action by process operator.
Pl. let me know whether someone has come across this above requirement & whether it is implemented using some custom script for Acknowledge All button.
Regards,
Rishi.
Hi Rishi Sir,
Create a replice of the alarmList.grf and configure the grid display such that only Warning (Value=11) Alarm Entries get populated in the display .
This way the user will only be able to acknowledge Alarm Entries of Warnings and Critical Alarm Entries would remain intact.