Unable to unassign a license from nodes

I'm unable to unassign licenses from my database.

In DeltaV explorer they're still assigned but when I choose unassign a license from the node on Control Network, nothing appears,

Any solution?

Scenario: I need to change licenses after a developer key expired

*** Sorry for bad brazilian english

Thiago Borba
| +55 21 2263.3549 | +55 21 99339.2221
yukon.net.br

  • Hi
    All license type are not un-assignable
    Case 1: license you can unassign: from dv explorer go on the node in the tree below control network , right click un assign etc etc.

    Case 2 : this a license which can not be un assigned, make an fhx export of the node , delete the node (at this point license will be released and available in the license basket) import back the node from fhx. The node will be imported but without license assign to it.