Hi,
The AI faceplate we have right now has the blue color bar. The customer want the bar to change color when PV is in alarm. According to the alarm priority, bar changes to color of same alarm color, yellow for warning, red for critical, etc. The control module I have is just a AI block. Could someone help me on what data source should I link to?
Thanks a lot!
May
Hello!
I can suggest to use DVSYS.@MOD@/ALARMS[1].F_PRI. It returns value from 3 to 15 or 255 and alarms must be created in a Control Module
I hope I was usefull to you!
In reply to May:
May, the information on the ALARMS parameter is in BOL. Search for "the ALARMS Parameter".
Note that this parameter is derived from alarm data at the console. It is not available at the Control Module Level. The Workstation Alarm system uses alarm data from modules and creates this parameter for use in displays.
In BOL in the section above, there are tables that break down all the attributes. ALARMS[ ] is am array of the applicable alarms for the User, Area and Module, up to 250 alarms in the array.
Andre Dicaire