Emerson Exchange 365
Search
Sign-In / Register
Site
Search
Sign-In/Register
Services
Products
Control & Safety Systems
Asset Management
Measurement Instrumentation
Valves, Actuators & Regulators
Fluid Control & Pneumatics
Electrical Components & Lighting
Welding, Assembly & Cleaning
IIoT & Digital Transformation
Industries
Chemical
Food and Beverage
Industrial Energy
Life Sciences
Oil & Gas
Power
Refining
Other Industries
Women in STEM
Events
Düsseldorf 2024
Immerse - Anaheim 2023
Grapevine 2022
Nashville 2019
San Antonio 2018
The Hague 2018
World
China
South Korea
Russia
More
Cancel
Products
More
Control & Safety Systems
DeltaV Forum
How to move a value?
Forums
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Recent Control & Safety Systems Discussions
TreyB
22 Apr 2024 9:47 PM
DeltaV Live Gem Read only after reinstall, etc.
9 Replies
TreyB
13 Apr 2024 3:46 PM
Control Studio Phantom session issue
2 Replies
Petrisky
12 Apr 2024 6:21 PM
Every (as in 300) LS DO CHARMs FAILED
5 Replies
Verx
12 Apr 2024 5:53 PM
DeltaV PK Controller EIP To Wago 750-363
5 Replies
TreyB
2 Apr 2024 9:14 PM
Domain/Local Accounts
0 Replies
<
>
Similar Posts
Is there a way for a picture to move on a value or condition?
Moving test work
Alarm Priority moving
Moving to Electronic Batch Records
Moving Modules To Another Area
Share
Not Answered
How to move a value?
How can I move a value of flow totalizer at particular time?
2 Replies
THENNARASU R
17 Mar 2020 9:15 AM
Use TIMER, ACTION or CALC Block
1. Create a Output Parameter "FLOW_STORE"
2. Add TIMER Block and set a specific time
3. Add ACTION Block and write expression like
IF "Timer Output Parameter" THEN
FLOW_STORE := Totalizer value;
END IF
4. once complete, click the "Parse" button. error must be zero then only your expression is fully correct.
gamella
17 Mar 2020 10:08 AM
As "a particular time" do you mean a TOTAL value from the past is required???
If so, you can use a DT block (Dead Time function block). Wiring INTEGRATOR block OUT into DT/IN and setting desired delay X into DT block provides TOTAL value X seconds in the past.
With this you don't have to wait for X time intervals to get a new value. Notice that DT supports download without resetting t's critical values so you don't need to wait for X time after a download to get first "good" value.
DT block also provides some useful functions, as FOLLOW_IN. When this is set to TRUE, DT/IN is passed to DT/OUT without delay, allowing to activate delay programatically. (Check books online to get better understanding on Dead Time Block(