Hi,
My query is about using FORCE SETPOINT in EDC block.
# It work as
When FORCE_SP_D transition true from false (PED), Force_SP_VAL get copied in SP_D/ CAS_IN_D (depending on mode and device option selected)
# Books online says ;-
It will work even when CAS_IN_D/SP_D wired externally
# Practically observed (test module image attached)
1. When SP_D and CAS_IN_D wired externally, Force_SP_val don't get copied
2. It never get copied because i have written a ACT block even to test if it is written (And i am not able to see it online because it is over written by external link) but it was not.
So am i right on my observation or missing something ?
THANKYOU