I'm attempting to configure a normally closed valve to revert closed 15s after being given an open command. This will be the normal transition every time; Valve commanded open, 15s later needs to revert to closed.
I'm in DeltaV 12.3.1 and the valve module class is S_V11_IP_120
My thinking was to use force setpoints.
Where is the function for enabling "force setpoint in auto"? How do I enable it. Also will I need to suppress the "process action in auto" alarm once it's enabled (since the action is considered normal)?
Larger question - Is there a better way to do this?
In reply to Matt Stoner:
Thanks Matt. I found FS_IN_AUTO, and set to true. I will be testing asap. Regarding the second option, the valve is fail closed, and only has a closed limit switch. There is no confirm after command to open, only that the zsc is unmade - so I'm not clear if 'Passive when confirmed' is an option. It's a small valve, I would expect it opens within 5 secs.
In reply to SimHogan: