I have a couple ph control loops. It was requested of me to change the incremental on the faceplate to allow them to increase/decrease in .01 increments. I have done that, by creating specific faceplate for these two items. in my pro station it works fine. but for some reason, at the ops station, everytime they click on the loop, it says the faceplate cannot be found. I have gone to the pro plus station under deltav data/graphix/pic/faceplate/ and the exact faceplate is there. so I don't understand why they can't see at the ops station.
In reply to Mark Bendele:
In reply to Tom Light:
In reply to Maarten van der Waal:
DeltaV Operate requires a restart in order to load in any new faceplates. Not a windows restart but just DeltaV Operate