So when I have some new MQ controllers in hand I want to swap them out for existing MD (not MD+) controllers. The MD controllers are doing fine; I'm just doing this gradually over the next few years in preparation for v14.
Aside from the basic precautions e.g. upload controllers, backup database, etc. are there any concerns about this change? Is it indeed a "drop in" replacement?
In reply to chessley:
That was a very good advice by the LBP giving that there are some codes that is supported in the MQ controller that is not supported in the MD which could cause the switchover to fail or there will be a bump in our process. Here is the DeltaV Controller Redundancy info:
http://www.emerson.com/documents/automation/57664.pdf
In reply to Tinh Phan:
So I would do this with the process down? . . . wouldn't the procedure be
1) Swap out "standby" MD controller for new MQ
2) Once transfer of configuration is complete, status will show "partner available"
3) Force redundancy switchover
4) Replace the (former) primary MD controller
In reply to John Rezabek: