Dear DeltaV Specialists,
we supports a customer since years, his plant was running with DelatV 10.1 with MD+ Controller and last year the Plant was migrated from Emerson on Virtual Server with DeltaV 13.3.1.
Since this upgrade we have a sporadic problem which occurs on different Heat/Cooling System on different reactors.
Explanation:
When Heating Valve is open (Position Switch), cooling valve is interlocked (BFI Block).
When Cooling valves is Open, heating valve is Interlocked.
That always works fine and synchronous in the past: Close H valve and Open C valve.
Now the H Valves is opening and the C valve is not Closed, then the Equipment goes to Hold...
We tried to put a delay (10s!) in CND Block but that is not the solution for us.
In the past it worked without delaying the interlock Conditions.
Have somebody a ID?
Thanks