Hi All,
I have a step in a command driven SFC that has multiple actions inside it A1 to A10, what I am trying to achieve is a 15 second delay between each action as I have shown below.
I have thought about adding an extra action between each one to delay for 15 seconds but I was wondering if there is an easier way using the Delay Qualifier or the Time Limited qualifier?
Action A1 completes
Wait 15 secs (would be good if I could use a parameter to define this wait time)
Action A2 completes
Wait 15 secs
Action A3 completes
and so on and so on, any help would be greatly appreciated.
Save the Current step time into a parameter in the action and on the confirm wait for the current step time to be >= Parameter used + 15. Expression: '^/TIME_SAVE.CV' := 'STEPNAME/TIME.CV'; Confirm: ('STEPNAME/TIME.CV' >= ('^/TIME_SAVE.CV' + 15))