Hello,
I made an user defined export of an instance. Then I made some BulkEdit changes. Once I imported edited file, no changes were stored in the database. The same situation occurs when I make some manual change opening FHX in notepad. The only way to make it functional is to completely remove an instance and import edited file. Then it works. Any Idea how to fix it? We have 11.3.1 with latest hotfixes.
Regards
In reply to JDWheelis:
In reply to Youssef.El-Bahtimy:
Just change the 'time' value: so changing ' user="MyUser" time=1557994607/* "16-May-2019 10:16:47" */' to ' user="MyUser" time=1557994608/* "16-May-2019 10:16:47" */' is sufficient. The part '/* "16-May-2019 10:16:47" */" is just a comment.