Hello, I have a project where I have a CIOC pair with two baseplates. Along with this is an ASCO 580 manifold with 10 solenoid valves. I'm wondering how I configure the valves in DeltaV Explorer. I couldn't find any info in Books Online. Should I just configure them as if they are on baseplate 3? Does the manifold assembly have an address plug?
In reply to Rune Reppenhagen:
In reply to ajellis:
Hello, As Rune mentioned, the valve manifold will start at baseplate #8. You can either count from 12 to 3 or 1 to 10. Here is a link to the CHARM technical document ( ) Mapping instructions start on page 27. Hope this answers your question.
Regards,
Mukta
In reply to Mukta Sharma:
In reply to Donal Costello: