Hello all,
A query on downloading of Electronic Signatures. More so the type of downlaod that is sufficient.
BOL under the heading "Assigning policies to modules" states:
"Once a policy is assigned to a module and the module is downloaded, signatures will be required for writes to the module parameters specified in the policy."
Our findings:
Once the policy is assigned to the module (test system) and a download of "Changed Setup Data" (CSD) to the ProPlus is complete, the Electronic Signature is active.
After policy assignment (or after chage to an existing policy) a download of CSD to the PP appears suficent. ("Module Table" is downloaded)
Downloading a module also downloads the "Module Table"...as well as downloading the module.
If possible we want to avoid module downloads as this affects running items.
(In our case we use a policy: field "NALM".)
Do any forum members have experince to share on what type of download works with Electronic Signatures?
Is "Module Table" the key?
Is there a DeltaV'ism why the module must also be downloaded?
(Not finding this reason in BOL).
Thanks.