Hi,
I am trying to use electronic signature, there is requirement to apply this only for 2 parameters in the module, however when I enabled electronic signature thru library for this module, electronic signature gets applied to all parameters in that module. even though only required parameters are listed while configuring new signature. If anyone have any idea about how to apply this function only for selected parameters and not for all can share the knowledge,
Thanks in advance for reading the question,
Chaitali!
Do you have a field configured for your policy? Per books on line article Signature Policies:,
Note
The signature policy for Field Confirmation takes precedence over the policy for Parameter Confirmation even if the Field Confirmation requirement is less stringent than the Parameter Confirmation requirement.
So if you have CV specified for the field, then all parameter writes to the CV field will have the policy imposed, regardless of which Parameters you have specified.
Remove the CV field from the Field Confirmation policy and the policy will only use the parameters specified.. You typically would only need this for unique fields like those having to do with alarming like *ALM and *ACK.