DLL file loading failed while opening operate in configure/run mode in DV version 13.3.3

Hi,

I'm facing issue while opening operate in both configure & run modes, I coped complete graphics I-fix folder from working station but still the error persists.

I have SIGlobal_SIS.fxg in it and I tried adding its references by following procedure from PCSD_Procedure_SIS_Displays.grf file while it did not succeed as it ran into script error multiple times.

Sharing some snaps of errors ( not very clear )

Looking forward for the help.

2 Replies

  • Don't copy complete graphics ifix folder, they are system specific files to the workstations in the folder.

    Copy only those relavent graphics and related files into the system graphics ifix folder(whichever applicable sub folder)

    Karma doesn't have any menu, you get serve what you deserve.

  • Hi
    Try to execute the ReRun workstation program.
    In the future, never copy this kind of file from a machine to another, especially for files related to SIS.
    It's very risky.