Hi,
I have an issue with a event flooding Process history every 10 seconds...
03/02/2018, 08:56:45, EVENT, AREA_A, PPLUS01, COLD_RESTART, DOWNLOAD, Cold restart on CTR01 failed; download data incomplete02/03/2018, 08:56:45, EVENT, AREA_A, PPLUS01, COLD_RESTART, DOWNLOAD, Cold restart on CTR01 started
The event started following a partial download to a AI module - simply a change to the HI_LIM parameter.
At the point of downloading, I receive the following warning dialog...
WARNING:CTR01 has one or more system files missing which could impact the integrity of controller redundancy. Perhaps, another download is in progress.
To check the powerup directory in more detail, run the Diagnostics application and use the Powerup Directory Test tool.
The Powerup directory test of CTR01 shows that the majority of items in the Powerup directory differ from the controller. Exceptions appear to be any itmes recently downloaded.
The controller (SX) cold restart source is "Controller"; User Restart State is "Yes"; Cold Restart State is "No"
A total download to the controler stops the cold restart events appearing in the log, but I'm trying to understand why the controller is getting into this situation in the first place?
Is the Powerup directory mismatch related to the coldresart event appearing in the event log?
Thanks for any pointers
Andre Dicaire