I am enabling some thresholds inside the control module (LO_LO, HI_HI, etc)

In version 12.3.1, I am seeing:

THRESHOLDS$TH$ENABLE (Groupname IO) and THRESHOLDS$TH_ENABLE (Groupname Tuning)

What is the difference?

1 Reply

  • That is an error in the Class allowing configuration of THRESHOLDS$TH$ENABLE as that parameter will be overwritten by the wire from THRESHOLDS/TH_ENABLE parameter.

    You only need to configure THRESHOLDS$TH_ENABLE and should ignore/remove the THRESHOLDS$TH$ENABLE configuration.