Hi all,
is it possible to filter out SIS Hardware Critical alarms (12, 13, 14, 15) from alarm banner?. tried setting its Alarm Threshold to 15 but still getting an Annunciation. it does filter out all other alarm priority except for Critical.
Thanks.
Can you confirm you took the following steps to create and configure a workstation settings file?
1) Use DeltaV Operate (Configure) to open UserSettings.grf for some script editing.
a) If this picture does not exist, it can be created by saving a copy of User_Ref.
b) You can have a settings file for a particular workstation, by giving the file a name {computer name}_Settings.grf
2) Right mouse click in the open green space of the picture to access the context menu, then select Edit Script
3) Use CTRL-F to open the search dialog and search for "threshold".
4) Follow the instructions to set up the banner thresholds, noting the following:
a) You will need to uncomment one line and comment-out another
b) You will need to uncomment the thesholds for the six alarm sources and set them as you'd like, noting that the priority must be greater than the number value entered to appear in the banner. I.e. a setting of 3 allows all alarms of 4 and above to appear on the banner and a setting of 15 eliminates alarms from that source completely ... or at least should unless there is something special about the SIS Hardware thresholds that I'm unaware of.
5) Save and close the project.
Let us know if you tried this. In parallel I'll touch base with the DeltaV Test organization to see if there is perhaps something special about prority 15 for SIS alarm sources. If there is, I'll come back with a follow-up post.