Hi,
We are configuring a control module, for instance standard PID: FIC101 module with HI, HIHI, LO, LOLO, Deviation, IO BAD, Simulation alarms. We would like to have a control module level parameter that can tell this FIC101 has any suppressed alarm(s) in general, whether the alarm(s) active or inactive.
OPSUP is parameter field and if we use this parameter field we have to configure for each alarm type. For example, an FIC101 module, we have to configure FIC101/HI_ALM.F_OPSUP, FIC101/HI_HI_ALM.F_OPSUP, FIC101/LO_ALM.F_OPSUP, FIC101/LO_LO_ALM.F_OPSUP. For some plants, they have custom alarms added with standard alarms. If we follow method of using OPSUP parameter field, this would increase significantly the datalink counts for one graphic.
Our goal is to place a dynamo on graphic that will have a colored box around it, whenever assigned module has any suppressed alarm(s). This will raise the awareness of operators during normal operation, without checking Suppressed Alarm graphic.
Any ideas would be much appreciated.