Does anyone know how I can alter the PHVE Documents located in DVData-Charts-lib? I am looking to change the plot method for MOD/OUT.CV, when phve is lauched from the trend is plotted as step regardless of the method selected in control studio. When I launch the document or template from the lib folder and select the parameter I would like to alter, the option to change the plot method is grayed out. I may be going at this wrong so any ideas or direction would be appreciated, thanks in advance!
-Chris
Open the standard chart from within PHV (File -> Open -> AI_fp.phve) and make modifications, then save. Any module referencing the lib phve should be updated.