Downloading class based EM instances one-by-one

Hello,

I was wondering if it is possible to import class based modules into an existing system and download each of the instances of the class without having a dialog that prompts to download all of the instances at the same time. The process would go down in the event of every EM going down for a download, so each one should be downloaded individually. The user system is DeltaV 13.3.1

Thanks

3 Replies

  • Hello,
    With DV 11.3 it ist not a Problem. After Import you will see the blue triangle on every EM's which have tout be download. You could download them one by one.
    Regards
  • Are there linked composites in the modules that were also updated during the import? Class based modules don't usually require you to download everything at once of that class, but a linked composite update does.
  • In reply to Matt Forbis:

    Yes, there is a linked composite fail monitor which I did not change the structure, but did change a fail process condition from the library default of false to a parameter to monitor.