Hello All,
It was determined that the Mode needs to always be shown on the graphic for all Controllers, Valves, & Motors. (Not just during an abnormal condition)
Using OUR MODIFIABLE "AnalogInfo" GEM as an example, under Graphics Configuration / Extended Configuration / Mode Indication / **Change selection from (ABNORMAL TEXT to ALWAYS)**.
The change was made and saved using the GEM CLASS TOOL/ GEM CONFIGURATION DESIGNER/ MODE INDICATION / DEFAULT where it was changed to ALWAYS.
This only changed the setting for the New Instances of the GEM from the Palette and not the Existing Instances on the current graphics.
Is there an easy way this change can be propagated out to the EXISTING INSTANCES?
You would have to manually change each GEM instance or export the displays, modify the file (which is an XML format so use something like Notepad++), change the appropriate values, save and re-import and overwrite with the modified XML file.
In the below snaps you will see a section of the XML for a display where you can see the correlation to the GEM configuration options. I'm not sure how your GEM you are using is built but this will show you most likely how to figure out what you need to change your export values to.
Just be very careful and you can mess up the XML and it may not import or may import and mess things up. Suggest keeping the original export and creating an updated one to import so you have a backup if you choose this method!
In reply to Matt Stoner: