Accessing Module Tags in Referenced Modules

Hello,

I currently have a module (Module A) that has a set of external references to other modules. I would like to be able to access the module tag name of these referenced modules, so that they can be shown on the faceplate of Module A. Is there an easy way to do this? I tried to access it directly through a parameter but was unable to. 

2 Replies

  • Hi, I dont know if I understand you, but if you need acces to a module tag from a faceplate, only you need modify the faceplate, adding the reference directly in faceplate.
  • OMB,

    Try the suffix ".A_$REF" to get the tag name as a string from an external reference.

    If you have an external reference in MODULE_A called PARAM1 that is pointing to the parameter PARAM2 in MODULE_B. In the faceplate of MODULE_A an alpha-numeric datalink with the source "DVSYS.@mod@/PARAM1.A_$REF" would display the text "MODULE_B/PARAM2" on the faceplate.

    If you want to pull out the module name only then use some code in the faceplate's initialize routine like the split function to write the result into a variable and display its contents as a datalink on the faceplate. Don't forget the datalink needs ".currentvalue" at the end. Here is an example of the code. You could extend it to read through a series of references.

    I hope this helps.

    RP

    Private Sub CFixPicture_Initialize()

        On Error GoTo ErrorHandler

        'Display external ref source modules
        Dim lngCmdStatus As Long                                'Status of module parameter read (0=good)
        Dim sLink As String                                     'Contents of parameter read
        Dim sTag As String                                      'Name of parameter to read
        Dim sAddress() As String                                'Array to contain address from external ref

        TGCounter = 0

        sTag = Me.ps_nm.CurrentValue & "/PARAM1.A_$REF"         'Assemble string to read module description
        sLink = frsReadValue(sTag, lngCmdStatus)                'Read module description into sDesc
        If lngCmdStatus = 0 Then                                'If read is good proceed, otherwise do nothing.
            sAddress = Split(sLink, "/")                        'Split address using / delimiter
            Me.ps_Param1_Address.CurrentValue = sAddress(0)     'Read module name from before / into variable and ...
        End If                                                  '... display in datalink on faceplate

    Exit Sub

        ErrorHandler:
            frsHandleError

    End Sub