Wireless gateway RS-485

I've heard we can use wireless gateway as a RS-485 host. I mean we can connect RTU devices to wireless gateway and transfer datasets to DeltaV system. Is this correct? has somebody worked on this?

1 Reply

  • The host part means you can communicate to the wireless gateway using a Modbus interface (Serial RS485), the gateway collates data from wireless devices and provides data to a Modbus host. It does not allow you to connect a Modbus RTU device to DeltaV wirelessly.

    You can use other devices (MOXA, Lantronix, etc.) to haul serial Modbus devices via wifi, but this is not that kind of device.