Launching PHV (Events+Chart) Requires Excessive Time Deltav 11.3.1

hi 

as i said in the subject i have problem with launching historian E+C and it takes time to open.i check that in the kba AP-0800-0056 that referenced the hotfix to resolve this issue for DeltaV 9.3.1 . i want to know that is there any kba reference for 11.3.1? 

please help me to resolve this issue.

thanks in advance.

2 Replies

  • Hi,

    There is a KBA for performance Limitations which is AUS1-115-990607142410. If you are in domain environment it might help to add the 10.4 and 10.8 networks to the reverse lookup zone of the DNS server.
  • In reply to Pieter Degier:

    HI
    my system configured to workgroup .as far as i know kba AP-0800-0056 for DeltaV 9.3.1 did not point to DNS server configuration . it references special hotfix that can afford this issue.
    can to you reference me that hotfix for 11.3.1?

    best regards.