I tried to import my plant database to new proplus workstation because my last one crashed .
When I try to import to new database it is imported but with some errors. I checked imported database and I saw these problems whit my database:
1-there are not my plant libraries in the composite and module templates
2-all areas are completely empty (there are no modules)
3- sis network doesn’t contain any SLS controller(I have enabled DeltaV SIS in the system preferences)
I have to say I configured the new proplus from beginning.
I was wondering if help me to solve this issue.
Thanks in advance
You can check the file ":\DeltaV\DVData\ImportExportProgress" to see specific errors. My first guess is that the user account that loaded the FHX did not have any SIS privileges and therefore none of the SIS came in.
It seems there is a bit of a curve ball with respect to importing SIS information from an *.fhx file of an entire database. In the new database you need to be logged in with a username of a user in the *.fhx file that has SIS privileges. For example. You have an empty database and you create NEW_SIS_USER with SIS privleges. As NEW_SIS_USER, you try to import the *.fhx file that has the whole database (users and SIS information included with the database). The import seems to strip off the SIS privileges from the NEW_SIS_USER account and the SIS does not come in.
I think you need to log in to DeltaV as one of the SIS user accounts in the import *.fhx file for the system to import the SIS information.
In reply to DBacker:
Did you migrate your databse?
In reply to samy:
Andre Dicaire