I need to move a system with VCAT enabled to another computer. Is there a way to keep the VCAT history, i.e., the current VCAT versions and comments of the existing database?
Thanks,
Quyen
In reply to Jason.Brumfield:
In reply to Quyen Dinh:
Yes the VCAT database is separate. In the database administration tools, you would archive your existing VCAT database, then on the new server, you would restore the archive utilizing the restore VCAT database tool. You will need to migrate the VCAT licensing as well or buy another license if you plan to have it active in both places.