Please share if you have any data about Availability and Reliability regarding DeltaV DCS.
Thank you in-advanced
Availability and Reliability are often misunderstood. Here are the definitions I use: - Reliability: Operating Time/ Number of Failures. ( MTBF, Failure Rate (λ)) - Availability: Up Time/(Uptime +Downtime). (Downtime is often referred to as MTTF) Emerson does not release individual component MTBF data for the DeltaV DCS. System Availability is calculated for customer systems based on specific system hardware designed to meet process applications and an appropriate estimate of MTTF, typically 4 hours. MTTF is determined by the end user and their ability to diagnose and repair an issue with the system. The availability of Spare parts on hand plays greatly to this number.
Different manufactures calculate MTBF data differently. The more common method is a parts count method based on MIL-HDBK 217, and the source data can come from different reliability databases, which differ from each other. After a significant number of components have been in operation for a minimum time, actual failure data may be used to represent MTBF. Different manufactures may use a different nominal operating temperature for their MTBF number. Comparing components from different systems would yield misleading results if values were not normalized. DeltaV uses 50 C. One Power Supply manufacture uses 40 C. MIL-HDBK 217 references 25 C in its discussions. A DeltaV component MTBF at 50 C would be over 5 times greater if calculated at 25 C. Increased DCS system availability is achieved through redundancy. Failure of a single controller in a redundant pair results in no loss of availability. Some times, MTBF of a Redundant component is calculated based on the resulting availability, but in reality, redundancy does not increase reliability, and failure of a controller in a redundant controller pair is still a failure. The consequence of the failure on the system availability has been mitigated with redundancy, but the number of individual components increases, so overall, the failure rate of individual parts over time can be expected to be higher. That is why we use Availability as the measure for the system and Reliability for the individual components. Availability also requires a definition of what it means for the system to be available. In reality, the availability of a control system is dictated by the availability of the instrumentation. Loss of a particular transmitter means that signal is no longer available, regardless of what the DCS IO availability is (simplex or redundant IO Card). So the maximum availability of the control system is limited by the choice of instrumentation. The Availability of the DCS is designed to minimize the reduction in availability of the process. It cannot increase it! A typical definition of Availability is “No single point of failure will result in the loss of more than X field signals.” If the value of X is set to 1, then redundant hardware is required through out, from the IO card, Network components and controllers. Remember that failure of a transmitter will result in the loss of one field signal. The DCS cannot increase the availability of the transmitter. For process applications that have multiple trains, or have the capacity for manual operation and thus continue to be available with the loss of multiple field signals, the Availability requirement of the DCS may be relaxed and simplex IO may be appropriate. So when an Availability calculation is required on the DCS, Emerson uses the system hardware to determine the availability based on loss of one field signal with an MTTF of 4 hours. There are multiple factors to consider, beyond just the component MTBF, to properly calculate system Availability. If you need a calculation of Availability for your DeltaV DCS, please contact your local sales representative office to have this done for you.
Andre Dicaire
In reply to Andre Dicaire:
In reply to Riyaz Ali: