Dear all,
Does anyone know how to connect Windows Service 2012 R2 with DeltaV OPC server? I am asking this because DeltaV OPC remote.exe doesn't compatible with Windows Service 2012 R2.
Can i do something with OPC mirror?
Best regards and thank you,
Igor
Hi, there is another thread regarding this, basically DeltaV V12.3 contains a 64bit version of OPC remote for 64bit Windows Severs (W2K8 R2 and above). You should be able to obtain this from GSC.
http://www.emersonexchange365.com/operateandmanage/deltav/f/50/t/2112
In reply to AdrianOffield:
Thank you for answering! Sorry, what GSC means? I am using DeltaV 13.3, and as i saw, the OPC remote isn't compatible with W2012 R2..
In reply to Igor:
In reply to Lun.Raznik:
Andre Dicaire
In reply to Andre Dicaire: