Hi all,
recently, one of our client had an issue regarding the controller (DeltaV PID) response where it gives a large kick when the large/small SP is introduced.
PID setting: Reverse Acting; Gain = 10; Reset = 300
Scenario 1:
SP = 0; PV = 18.6; CO = 0%; Mode = Manual
STEP 1: Ops changed the mode to Auto, and changed its SP from 0 to 9 (SP change is introduced). CO jumped to 100% then slowly decreasing to 0%
Scenario 2:
STEP 1: ops changed the SP to 18.6, and then changed the mode to auto. CO remains the same at 0%.
STEP 2: ops changed the SP to 0, CO remains the same at 0%
STEP 3: ops changed the SP from 0 to 9, CO remains the same at 0%.
the question is, scenario 1 (STEP 1) and scenario 2 (STEP 3) have the same operator action but different result. i tried explaining the transition of modes and SP-PV tracking for bumpless transfer. any PID expert here?
In reply to GeloCortez: