• Not Answered

Online Control Studio

dear friend

I try to have online control Studio (application) from engineering work station (P Station), but I have error code 60 and 99. please see the below shots from system:

.

may I ask you please help me that how can I solve this problem?

please be informed, the communication between P Station with P+ station is OK and I can open DeltaV explorer from P Station, but when I try to go to Online in each control studio, this messages are appeared.

you kind support in this regard will be highly appreciated.

thanks and regards 

5 Replies

  • The message indicates that the module is not downloaded.
    You do not indicate the module is downloaded, nor whether the downloaded modulecan be opened online on the P+.
    Can you see the used controller from the P using Diagnostics?
  • In reply to Maarten van der Waal:

    Yes, I can see. all things are normal, even I can modify any control module(Studio) and I can download from P Station.
    Only, I can't see my control studio as Online in P Station.
  • In reply to Pouya:

    The second error indicates that the setup data has not been downloaded to the workstation and possibly pro plus. The module table is part of the setup data download. Select the workstation and proplus and select to download changed setup data.
  • In reply to Youssef.El-Bahtimy:

    dear Youssef

    actually, I downloaded the pro plus and workstations, but we have this problem yet.
    this station is a new one. I added it to system and as you know, before downloading pro plus, you have no access to download new workstation (it appeared as a offline system). when pro plus was downloaded, I had permission to download new workstation, then I downloaded the new workstation and all things were OK. communication, DeltaV Explorer and all other things were OK. even I can change control studio from the new station and I can see it in Pro Plus. Only in new station, I cannot Open the control studio in Online environment and the above Error are appeared yet.
    meanwhile, the HMI pages (in operator RUN) have no access to online data from controllers.

    Regards
  • Try enabling Auto Update from Proplus for all nodes & check.