I have a temperature control module 26TCA431B for a thyristor control panel. The module is always flagging PVBad_ALM when the thyristor is heating up. I checked the input IN which is AI/OUT of another module 26TI-431B and the module is OK. Process History view shows the PID PV value is fine.l Alarms configured for the 26-TCA431B are Hi-Warning, Lo-Warning and PVBad-Critical.
The blocks in the 26 TCA431B module are:PID1,CALC1, CALC2,RTLM, AO1, AI1.. The CALCs have expressions to decide how the PID/OUT is used to control the thyristor in the field depending on availability of generators
On the PID The OUT_SCALE is 0-100% and PV is 0-250DegC on the 26TCA-431B.I have checked diagnostics and nothing seems to be wrong. MERROR is Module Ok, MSTATUS is Abnormal Active and BLOCK_ERR is Simulate Active which I confirmed is due to Simulate -IN enabled for an AI block as part of the configuration.
The faceplate keeps flagging PVBad_ALM whatever the value of the PV on the PID. I checked the input module to the PID, a 26TI-431B and it appears fine.
Can someone tell me what conditions can result to this kind of Alarm. Every thing is running fine but this alarm will spoil my alarm rates after each shift.