Dear all
I am using delta v 11.3.1
I am facing a problem while reopening of control studio.
This problem is only for 3 nos of modules
Case-1
Once the module opened in offline/edit mode and closed it,
If I open it again then the control studio is found to be working normally.
Case-2
Once the module is opened in online/debug mode and closed then,
If I open it again the studio is showing the message Module being updated by administrator (in detail- unable to register to update an item)
I did following activities for primary checks
1) Checked database connections after closing the module.
It showing control studio is running. I disconnected it and try to open the module
It open once only and again shown the same error
2) checked CPU utilization.
Found normal like 5-8%
3) I have 3 GB RAM With a system.
4) Also checked the value of that particular module in opcwatchit and it showing "Good"
5) Cleaned and even extended cleaned the database
6) Delete the module from database and create a new one but still it gives a same message
7) Also installed updated hotfix
8) Closed cs.exe in Windows task manager.
9) Restart and download whole the system
Please suggest the solution for it.