Currently our DeltaV is setup to read data serially from a PLC.
How do I setup a module in DeltaV so that the PLC can read a AI or DO value from DeltaV?
Thank ou
In reply to Youssef.El-Bahtimy:
Youssef.El-Bahtimy said:It depends on the protocol and driver for the serial card. You have already stated that DeltaV reads from the PLC, so I will assume you have DeltaV as the Master and PLC as the subordinate. Technically, this means the PLC will not read from DeltaV but rather DeltaV will write to the PLC. You need to duplicate one of your existing serial datasets, change the direction from input to output, and adjust the special data and offset to point to the correct file number and register range. The details are likely documented in the serial driver documentation, but using your existing setup as a basis on of understanding is a good start. There are nuances regarding output with readback, sending outputs on start etc. that you will have to contend with as well, based on what your needs are.
Thank you Youssef
We have a virtual I/O module setup but only for AI and DI. How can I setup the modules of DO an AI?
Thanks
Thank you Youssef, I understand now.
I just need to:
1. Setup a new dataset on my serial I/O device already connected to the PLC
2. Set the dataset direction to Output
3. Obtain PLC settings
4. Setup the parameter type.
Basically, just like you recommended, use the Serial Input as a go by.
Thank you, kindly.