Hello,
Maybe I am confusing myself but I am trying to understand the difference.
I have a flow control application that will control flow at normal flow rate of 500pph (setpoint of PID set to 500pph in Auto at all times).
I have 3" Fished valve with rated Cv of 338.
My process conditions calculates the Cv to 223 and the valve will be 76% open at this Cv of 223.
My P&ID block will be setup for :
Outscale : 0-100%
PV scale: 0-25000 pph.
How do I calculate the valve OUT% at 500pph? My concern is that the valve will operate in the 0-20% open range while controlling at 500pph.
Thank you
In reply to leirbag:
In reply to Bruce Brandt:
Bruce Brandt said:If you actually have that broad a control range then you really should be considering putting in parallel valves where one is sized for the lower range and the other for the upper. I'd recommend sizing the small valve based on a max flow of 1000. As the other person pointed out you apparently are looking for control for a 50:1 range and no valve can do that. At best valves are able to do 10:1 and 5:1 is more probable without using some very special trim. If indeed you mistyped the upper flow value then you should talk with the Fisher person who sized the valve to determine which form of trim is installed. Again as leirbag points out Equal Percentage should give you good control without sitting on the seat all the time while linear will may also work but could still give some issues, certainly a quick opening trim will not work very well at all. What kind of valve is it? Globe? Ball? V-ball? Butterfly? Plug? That has a lot to do with the valves characteristics.
Thank you Bruce.
The valve was sized for 25000 pph max flow instead of normal flow of 500pph. The valve is a 3" equal percent ball valve.
I am trying to understand what role does the DCS PID control have regarding the CV percent openings?
Here is the sizing data:
500pph, Cv - 4.604, 15% open
25000, Cv - 223, 76% open.
In reply to DCS Newbie:
Best Regards,