Hi,
Do we have standard OAR summary (phases) graphic per unit wise from PCSD DV 11.3.1 for a non batch plant ?
If anyone has developed such a requirement of OAR summary graphic, kindly let us know the same / graphic.
You can take the Alarmlist.grf and do a SaveAs to a new graphic title (i.e. OARlist.grf).
Change the Graphic Title Text and remove the Unack, Total and Suppressed information.
Right click on the DeltaV Alarm Summary ActiveX object and select Properties...DeltaV.DVAlarmSummaryObject.
Go to the Filters Tab and change the Specific Priorities to only be the priority of the Prompt (Default I believe is 14 for 11.3, see below).
I have actually done something similar by embedding this ActiveX object on the Alarm banner and only showing the module name (Selected on the Columns Tab). Here is a view of one in Run mode (Customer wanted Orange to signify Prompt Active) and you can see more than allowable are active and a scroll bar allows operator to see all of them.
When the operator clicked the name in the OAR window, the display that is configure as the primary display for that items would be opened.
Hope this gives you some ideas of what you can do to accomplish your needs. Let me know if you have further questions
Regards,
Matt