Process History View Export

Hi,

At present we are exporting our process history view as an XML file at the start of each month. This is to assist with operations and their alarm management.

At present we use a the manual export at the start of each month to gather the previous months data. Would it be possible to automate this, either through Process History View, or through another method?

I’ve explored books online but can’t seem to find a way to carry this out.

 

Thanks.

 

Mike.

 

  • In reply to Lun.Raznik:

    The 'Export Alarm Summary to XML' button on the alarm list fires a application called 'AlarmSummaryUtility.exe' in the DV/bin folder. This program has many options (see /?). A simple command like: AlarmSummaryUtility.exe 100 /export will export the 100 most important alarms to a file. The resulting file can be timestamped, converted to Excel and compressed. Can be done in a windows batch file which can be scheduled as well.

    Also on the LinkedIn group there is a discussion about this topic. The suggestion there is to use XLReporter.

    www.linkedin.com/.../Im-looking-way-capture-DeltaV-1270757.S.46220538