Dear Experts,
I have this popup message " the picture just loaded into the main window is not a main window picture. Function that would normally replace the picture in the main window will no logger work...." whenever I load a graphic. what went wrong with my graphic, and how can fix this.
many thanks
Lihn
Could be many things....
1) Check to make sure you have the "grpVariables" group in the display and it didn't get accidentally deleted. You can get a copy of that from a working graphic.
2) You're on quadhead display and running version 11.3.1 without hotfixes. If so, need hotfixes loaded.