Hi, I have recently installed a Profibus DP Series 2 card on a system running DeltaV ver.7.3. But during hardware selection, I can only select Series 1. Any advice on this. Thanks
I have a customer that was on 7.2 for years, then upgraded to 11.3
In 7.2, explorer only had the choice for Series 1, even though they had Series 2 cards.
On their 11.3 system, the card is still listed as Series 1. In other words, I don't believe it makes a difference.
Ensure the card is ultimately flashed with the latest firmware (supported for 7.3) before placing in service.
Youssef El-Bahtimy | Systems Integration Technologist PROCONEX | 103 Enterprise Drive | Royersford, PA 19468 USA Proconex Office: 610 495 2970 | Cell: 267 275 7513
In reply to Youssef.El-Bahtimy:
have a look at KBA AP-0700-0106....basically Profibus DP Series 2 card will work fine on DV v7.*