Is it possible to password protect a faceplate.
In reply to AdrianOffield:
Hi Gary
Yes, you can imagine a passworded locked faceplate :
- Open a traditional faceplate according the module type and save it with a new name
- Select all graphical objects on the form and change the Layout owner, ie #2
- By using the "Set layer" icon, select the #1 : No object may appears --> Add a TextBox (Datalink with inplace on) + and Ok button, associate then to the layer #1
- In the Ok button script, modify the DisplayLayer to 2 if the entered password is correct
Don't forget to set the DisplayLayer to 1 in the "CFixPicture_Initialize"
Remember that DisplayLayer is a bit combinaison.
For layers 1 and 2, no difficulties, but the next one is not 3, but 4 (3 is layers 1 and 2 visible).
0 means all visible.
Of course, it's not very secure, but its a way to proceed easily
Regards - Jack