Faceplate

Hi

I have question if I want to open many faceplate in one Graphic how can programing that by graphic.

2 Replies

  • I dont know if I understood what you want exactly !! but I am assuming you want to keep the faceplate on the screen after opening. If that's the case then simply you have to pin the fp . If the pin does not exists then you have to go to the configure mode and add the pin to fp pic.
  • Are you by change looking for this which is found in Usersettings of DeltaV Operate Configure
    '===================================
    ' Faceplate Initialization
    '
    ' To enable multiple Faceplates, uncomment the following line.
    ' A pushpin will then be visible in faceplates. Push the pin in to
    ' keep the faceplate from being closed when subsequent
    ' faceplates are opened.
    ' DO NOT UNCOMMENT THIS LINE FOR OPERATOR KEYBOARD SYSTEMS. Doing so will prevent the Operator
    ' Keyboard faceplates from opening.
    '
    'frsVariables.GN_IA_LOCKENABLED.currentvalue = 1
    '

    Sal Salamone