s series controllers can be used in versions like 10.3 or olders??

S controllers can be downgraded to older versions of deltaV??  Thanks for helping me!!!

ypiedra

  • ypeidra - S-series controllers only work with DeltaV v11 and above; there is no way to flash them to earlier versions of DeltaV.  M-series controllers can be flashed to earlier versions of DeltaV if required.  In order to take advantage of electronic marshalling and the other benefits of the S-series, your best bet is to upgrade to v11.