Dear All,

During routine Diagnosis checks, one of the CSLS shows bad OINTG and when checking  it shows “SIS in Flow Control, module not excusing at scan rate”

the ZX controller connected to this csls  sw. v is 13.3.1.6364.xr

what might cause such issue? And how we can be solved ? 

thanks 

1 Reply

  • The CSLS can be configured to run at 50/100/150/200 ms, if the logic solver is set to run at 50ms, but the logic is to complex to run at that scan, it will automatically bump to the next scan, and this error will pop up. To clear that, you have to set the CSLS to run at the next scan rate and download it.