DeltaVSecure Parameters from one CSLS to other CSLS

Hello,

I want to know if there is any limitation on reading secure parameters from one CSLS to other CSLS?

Actually, I'm getting error "noComm LUV) for a Boolean secure parameter.

Let us build success,

Zohaib Jahan

4 Replies

  • Can you give us a little more information? Like maybe paste screenshots of the secure parameter and the reference on the other end in Control Studio.

    - Bryce H. Elliott, P.E.

  • , the is no, there's no limit on how many times a secure parameter can be subscribed, there are limits though on how many secure parameter a particular CSLS can publish, I would be surprised if you exceeded those limits.

    Can you give us additional information on how many Secure Parameters the source CSLS is publishing?

    Additional information that would be good to have is DeltaV version, and a description on the architecture.

    Rgs,
  • In reply to Bryce Elliott:

    Thanks for your reply. I skipped this thread notification. Solution which worked for me: I have to download LSNB as well apart from SIS node.

    Let us build success,

    Zohaib Jahan

  • In reply to Tadeu Batista:

    Thanks Tadeu for replying. The solution which worked for me: I downloaded both LSNB as well apart from SIS node downloading.

    Let us build success,

    Zohaib Jahan