How to commission 1420 WirelessHART gateway in DeltaV?

I have a 1420 gateway which connected to AMS and working properly. However, I have a problem to find the gateway in DeltaV. The gateway didn't automatically appear in the decommissioned nodes folder. What should I do to commission the gateway in DeltaV?

  • Based on your description you most probably have a Gateway that is not DeltaV Ready. When enabled, this function allows the gateway to communicate with DeltaV directly and show up in the decommissioned nodes list once first connected to the DeltaV system. Please check if the DeltaV Ready option is available within the firmware options section (using the web interface), and if the option is not available please reach out to our Wireless Specialists to get more information on how to get the option files to enable DeltaV Ready on your Gateway ([email protected]).
  • In reply to Alexandre Peixoto:

    It is also important to note that this will change how the Gateway integrates with AMS Device Manager. It should appear under the DeltaV Network when you rebuild/identify, but you need to manually remove it from the Wireless Interface.

  • In reply to Alexandre Peixoto:

    Yes, You are right. The DeltaV commissioner was dis-enable. After, I changed it and it works now. Thank you so much!!
  • In reply to Nicholas Meyer:

    Nike, you are right. DeltaV re-assigned the IP address after I enable the DeltaV commissioner in 1420 gateway. I already fix the IP address and it works in AMS and DeltaV now. Thank you so much!!