1420 Gateway OPC to DeltaV

I am working on intergration between 1420 gateway and DeltaV. I have one wirelessHART Power Meter with 24 auto burst variables reports to 1420 gateway. I would like to feed these 24 varaiable into DeltaV via 1420 gateway OPC protocol.

The problem is how to set up/ configure DeltaV system to pull the data from 1420 gateway? Is anyone done this before? Do I need to set up a OPC server to pull the data from 1420 gateway and feed into DeltaV as a bridge? 

 

  • Wireless Gateways with Native DeltaV functionality pass only the four primary HART variables directly through to function blocks. If you want to use other HART parameters, then you need to use OPC Mirror to mirror the 1420 OPC parameters into a DeltaV control module.