3051S DP Flow Meter Individual High & Low Side Readings

Are the high & low side pressure readings accessible via AMS or HART? 

3 Replies

  • For a 3051S DP transmitter, the individual static pressures for each of the transmitter typically isn’t measured; rather the DP is only measured. However if you have a 3051SMV, the static pressure is available in addition to the DP (you can get the other side by subtracting/adding the DP from the static pressure) which can be read via the digital HART or Fieldbus interface.
  • In reply to Wally Baker:

    Wally, which side is the static pressure sensor connected to?
  • In reply to Barry Payne:

    Hi Barry,

    The static pressure is connected to the high side of the transmitter.