Changing the colour on PID faceplate

Hi everybody,

We have recently engineered a project on a client's existing database. We configured the new section of the plant using PCSD modules and PCSD style graphics. 

I need assistance with changing the colours on PID faceplate to look at the PCSD colour table. The faceplate FFLP SP and PV bars are white, the customer wants these to match the PCSD PID faceplate, to standardise  the look across the graphics.

Regards

Lebogang 

1 Reply

  • These PV and SP rectangle 'Color' animation should have Data Source referenced to a String variable value in frsVariables. Also on Advanced tab check which Shared Lookup table is used.
    Check Data Source referenced in String variable (PV, SP) value in Shared Lookup table. A specific color will be configured with 'Exact Match' for that String variable (PV, SP).