Ran into a weird one this AM which I'd never seen until we upgraded our software and controllers to V14.3.1 and type MQ respectively. One of my controllers lost communications with an intermediate 8-Wide carrier housing 8 120 VAC Isolated input cards. Looked in diagnostics and all eight cards were showing as CFG Present but no card. My first instinct was to change out the carrier, which I did but which didn't rectify the problem. After checking a bunch of other stuff to no avail I decided to download the entire controller, which still didn't rectify the problem. I finally decided to pull the controller off the bus and put it back in. This worked but I'm thinking that the download should have taken care of the problem, or conversely, that it should never have occurred. Has anyone else run into this?